          I'm having some reliability issues with my motion sensors I keep seeing the subject message and I don't understand what it is trying to tell me.  This is what I'm seeing in the logs:
           | Posted: January 26 2015 at 09:55 | IP Logged |   |  
           | 
 |  
 time_stamp     type  &nbs p;  event     info & nbsp;   sequence      ;dddisplay     pbcolor  & nbsp;  webcolor     pbbac kcolor     webbackcolor
 1/26/2015  09:44:18.328     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[0D.3F.BF] To Address:[1E.DC.90] Flags:[97] Cmd1:[19] Cmd2:[4].  Decode: ACK of Group Cleanup. From: MASTER BEDROOM LAMP To: POWERLINC MODEM Group: 4,  Off         &nb sp;479     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:44:18.14     31    ;  INSTEON PLM Controller PLM transmission of Address:[0D.3F.BF] Flags:[69] Cmd1:[19] Cmd2:[4].  Decode: Group Cleanup. ID: MASTER BEDROOM LAMP Group: 4,  Off         &nb sp;478     Insteon   Out     0    &n bsp;#000000     16776960   ;   #00ffff
 1/26/2015  09:44:17.546     31  &nbs p;  INSTEON PLM Controller PLM transmission of Address:[00.00.04] Flags:[207] Cmd1:[19] Cmd2:[0].  Decode: Group Broadcast. Group: 4,  Off         &nb sp;477     Insteon   Out     0    &n bsp;#000000     16776960   ;   #00ffff
 1/26/2015  09:44:17.515     28  &nbs p;  DAY       & nbsp;  476     User   Message     16777215  &nb sp;  #ffffff     32768&nb sp;    #008000
 1/26/2015  09:44:17.406     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[08.59.2F] To Address:[1E.DC.90] Flags:[33] Cmd1:[49] Cmd2:[0].  Decode: Direct ACK. From: MASTER BATH VANITY To: POWERLINC MODEM, Set Btn  LED         &nb sp;475     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:44:17.203     31  &nbs p;  INSTEON PLM Controller PLM transmission of Address:[08.59.2F] Flags:[5] Cmd1:[25] Cmd2:[0].  Decode: Direct. ID: MASTER BATH VANITY, Status  Req         &nb sp;474     Insteon   Out     0    &n bsp;#000000     16776960   ;   #00ffff
 1/26/2015  09:44:17.062     8    ;  Macro MBR-TIMER TO OFF  executed.        &nb sp; 473     Macro  & nbsp;  0     #000000  ;    65535      #ffff00
 1/26/2015  09:44:17.015     9    ;  Timed Event MBR-TIMER TO OFF  processed.        &n bsp; 472     Execute  Timed  Event     16777215    ;  #ffffff     32768  ;    #008000
 1/26/2015  09:44:03.234     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[21.5D.E3] To Address:[13.00.02] Flags:[195] Cmd1:[6] Cmd2:[0].  Decode: Group Broadcast. From: MBR-MS Group: 2, Grp Brdcast  Success/Fail           471     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:44:02.203     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[21.5D.E3] To Address:[13.00.02] Flags:[199] Cmd1:[6] Cmd2:[0].  Decode: Group Broadcast. From: MBR-MS Group: 2, Grp Brdcast  Success/Fail           470     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:44:02.109     11  &nbs p;  Trigger check of MBR-DARK TO LIGHT  performed.        &n bsp; 469     Trigger   Check     16777215    ;  #ffffff     8388608&nb sp;    #000080
 1/26/2015  09:44:02.015     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[21.5D.E3] To Address:[00.01.02] Flags:[195] Cmd1:[19] Cmd2:[2].  Decode: Group Broadcast. From: MBR-MS Group: 2,  Off         &nb sp;468     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:40:25.109     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[21.5D.E3] To Address:[00.01.01] Flags:[195] Cmd1:[19] Cmd2:[1].  Decode: Group Broadcast. From: MBR-MS Group: 1,  Off         &nb sp;467     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:39:54.562     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[21.5D.E3] To Address:[11.00.01] Flags:[195] Cmd1:[6] Cmd2:[0].  Decode: Group Broadcast. From: MBR-MS Group: 1, Grp Brdcast  Success/Fail           466     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 1/26/2015  09:39:46.656     11  &nbs p;  Trigger check of MBR-ON TO OFF  performed.        &n bsp; 465     Trigger   Check     16777215    ;  #ffffff     8388608&nb sp;    #000080
 1/26/2015  09:39:46.546     30  &nbs p;  Incoming Insteon received on INSTEON PLM controller PLM. From Address:[21.5D.E3] To Address:[00.01.01] Flags:[199] Cmd1:[19] Cmd2:[1].  Decode: Group Broadcast. From: MBR-MS Group: 1,  Off         &nb sp;464     Insteon   In     0    &nb sp;#000000     65280  &nb sp;  #00ff00
 
 Tom
 | 
       
        | Back to Top |     | 
       
       
        |  | 
        | BeachBum Super User
 
  
  
 Joined: April 11 2007
 Location: United States
 Online Status: Offline
 Posts: 1880
 | 
          Looks like you are getting multiple triggering from the motion detector. Try this fix from Dave:
           | Posted: January 26 2015 at 10:57 | IP Logged |   |  
           | 
 |  
 I call the macro TRIGDISABLE.
 
 Code:
 
 10 Formula Immediate ph_disabletrigger(ph_getvar_s(2,1))
 20 Wait ph_getvar_n(1,1)
 30 Formula Immediate ph_enabletrigger(ph_getvar_s(2,1))
 
 Whenever a trigger is fired, the ID of the trigger will be placed into the [TEMP1] variable. In line 10 of the macro, we can see that we will disable the trigger in the [TEMP1] var. Line 20 then waits for the amount of seconds contained within the [LOCAL1] var. If we call the macro from the trigger action with a ph_macroparm function, we can place this variable delay in the [LOCAL1] var. Line 30 then just re-enables the trigger after the wait time has expired.
 
 So, with this type of problem, we should be able to get by with a wait time of about 5 seconds. So on the Group In trigger, we can make the action:
 
 ph_macroparm("TRIGDISABLE",5,0,0,0,0) + whatever other action you really want to perform.
 
 
 
 
 __________________
 Pete - X10 Oldie
 | 
       
        | Back to Top |     | 
       
       
        |  | 
        | dhoward Admin Group
 
  
  
 Joined: June 29 2001
 Location: United States
 Online Status: Offline
 Posts: 4447
 | 
          Tom,
           | Posted: January 26 2015 at 11:56 | IP Logged |   |  
           | 
 |  
 In addition to what Pete wrote, the log looks pretty normal. Typically Insteon battery powered devices will automatically send the "group broadcast" command 3 times since its an unACKed command.
 
 In the log, it looks like motion was no longer detected so you got the MBR-MS Group: 1, Off (group 1 on the motion sensor is the "motion"). The next message is the Group: 1, Grp Brdcast Success/Fail message which will automatically be sent after any group broadcast (this is new message that only the newer devices now send...older devices won't send this message). You should be able to ignore it.
 
 The next message is another MBR-MS Group: 1, Off message. I didnt see a group 1 On message so that could potentially be a problem. However, I believe the motion sensor can be configured to send only ON or only OFF so that may be something to look at. I don't see the Broadcast Success/Fail message to go along with this so it may have been lost (possibly comms issue) or perhaps just not sent. The success/fail message I tend to ignore.
 
 The next message is the MBR-MS Group: 2, Off. Group 2 is for the light sensor in the motion sensor. Cant remember which is which but the light level in the room transitioned either from light to dark or vice versa. You've then got two of the Group: 2, Grp Brdcast Success/Fail messages to accompany the Group 2 Off message.
 
 All in all, it looks pretty normal. I would expect more group broadcast messages and I like to have my motion sensors configured to send an On when motion detected and an Off when motion has stopped and exceeded the timeout so you may want to see why you're not getting any On messages.
 
 Since it is an RF only device, you may be having Comms issues if there isnt an access point or dual band device nearby. You can try clearing the comms for the motion sensor and then placing it in link mode and then continually scan the database (drop the poll interval to 1) 10 or 20 times and then check the comms report.
 
 Dave.
 
 | 
       
        | Back to Top |       | 
       
       
        |  | 
        | BeachBum Super User
 
  
  
 Joined: April 11 2007
 Location: United States
 Online Status: Offline
 Posts: 1880
 | 
          
           | Posted: January 26 2015 at 12:47 | IP Logged |   |  
           | 
 |  
| dhoward wrote: 
 
    
    | 
      
       | The next message is another MBR-MS Group: 1, Off message. I didnt see a group 1 On message so that could potentially be a problem. |  |  |  
 Dave, I have been experiencing some of this missing GRP on and/or GRP off. Using multiple triggers along with Insteon traces I'm trying to trap it to see where they are lost. This is using an I/O LINC with my own sensor circuit. More later on a different thread.
 
 __________________
 Pete - X10 Oldie
 | 
       
        | Back to Top |     | 
       
       
        |  | 
        | Viper Groupie
 
  
 
 Joined: January 14 2007
 Location: United States
 Online Status: Offline
 Posts: 88
 | 
          Pete,
           | Posted: January 26 2015 at 13:10 | IP Logged |   |  
           | 
 |  
 :-)  Been there, done that.  Here is the Boolean value for my "MBR-ON TO OFF" trigger:  ph_disabletrigger("[TEMP1]") + ph_enabletrigger("MBR-ON TO ON") + ph_modifytimedevent("MBR-TIMER TO OFF", 1, ph_relativedatetime(today(), 4.5), 6) + 1
 
 I've got three triggers.  One handles Off to On, another On to Off, and another On to On. Multiple on or off events show up, but the triggers only fire once.
 
 Dave,
 
 I clipped the log so all you saw was the Off and the Grp Brdcast Success/Fail messages.  The On occurred earlier.  However, the Grp Brdcast message in the middle of the multiple Offs makes me wonder if the second (or third) Off took a long path to PowerHome.
 
 I'll keep looking at communication interference.
 
 Tom
 | 
       
        | Back to Top |     | 
       
       
        |  | 
        | Viper Groupie
 
  
 
 Joined: January 14 2007
 Location: United States
 Online Status: Offline
 Posts: 88
 | 
          Dave,
           | Posted: January 26 2015 at 13:33 | IP Logged |   |  
           | 
 |  
 Also, I hadn't paid attention when I replaced the Motion Sensor a while back and didn't notice the Grp Brdcast Success/Fail messages till I recently started having some issues.
 
 Tom
 | 
       
        | Back to Top |     | 
       
       
        |  | 
        | Viper Groupie
 
  
 
 Joined: January 14 2007
 Location: United States
 Online Status: Offline
 Posts: 88
 | 
          I moved an Access Point and now it appears PowerHome is seeing more of the messages.  I can see that the first byte of the To Address of the Grp Brdcast Success/Fail messages seems to be the command code.  I can't help but wonder if that should be used to help determine the state if the Grp On or Grp Off haven't been received?  Here's my latest trace:
           | Posted: January 26 2015 at 14:19 | IP Logged |   |  
           | 
 |  
 
   
 The triggers for MBR-MS aren't firing right now because they were disabled when the room got light from the sun.  They will be enabled when the room gets dark.
 
 Thanks to both Dave and Pete!
 
 Tom
 | 
       
        | Back to Top |     | 
       
       
        |  | 
        | dhoward Admin Group
 
  
  
 Joined: June 29 2001
 Location: United States
 Online Status: Offline
 Posts: 4447
 | 
          Tom,
           | Posted: January 26 2015 at 18:29 | IP Logged |   |  
           | 
 |  
 Glad to hear you're getting more reliable comms. Just
 so you know how to interpret the Broadcast
 Succees/Fail message, here's a little info.
 
 The To Address consists of 3 bytes. The first byte is
 the command (in hex) that is being cleaned. The Off
 command is 19 decimal, 13 hex so you know which
 command the success/fail belongs to. The middle byte
 is the number of devices that need to be sent
 cleanups. I find it odd that it shows 0 as I would
 expect it to show 1 for the PLM. Anyways, the third
 byte is the group number. The Cmd2 is the number of
 devices that failed the cleanup so a 0 is good.
 
 Not sure how useful the info is. The main thing I
 would look out for is getting a success/fail message
 but NOT seeing the Group Broadcast message that should
 have preceeded it.
 
 Dave.
 
 | 
       