Subject Topic: overload of Direct ACK Post ReplyPost New Topic
Author
Message << Prev Topic | Next Topic >>
andyR
Newbie
Newbie


Joined: April 07 2010
Online Status: Offline
Posts: 15
Posted: April 07 2010 at 23:21 | IP Logged Quote andyR

A question from a new powerhome user:

I'm getting a lot of Insteon In 'Direct ACK' events in my event log (on the order of 10-20/min) so that powerhome performance seems to be degraded, not to mention my events log blowing up. Any ideas on how to stop these? I seem to remember reading something about this in another post a month or two ago, but I can't find it any more.

Here is a sample of one of these events:

Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[XX.XX.XX] To Address:[YY.YY.YY] Flags:[33] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: UPPER HALL SOUTH To: POWERLINC1, Peek Addr


Thanks in advance for any help you can give.
Back to Top View andyR's Profile Search for other posts by andyR
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 08 2010 at 02:11 | IP Logged Quote grif091

The message is a response (ACK) to Powerhome2 Peeking data (cmd1:43 0x2B - read data) from memory of UPPER HALL SOUTH.

Since Powerhome2 does not create Event Log entries for background activity such as reading a device link database this should be coming from something that was initiated from a Timed Event, Trigger or Macro. What else does the Event Log indicate is going on at the same time. The message before this one should be an Outbound Direct message with the actual Peek address that is being read. All I can tell from the ACK is that a byte of 00 was being returned but not from what memory location.   Knowing the sequence of memory addresses that are being accessed may also provide some clues as to what is being done.

Also, what type of device is UPPER HALL SOUTH.

Edited by grif091 - April 08 2010 at 02:13


__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
andyR
Newbie
Newbie


Joined: April 07 2010
Online Status: Offline
Posts: 15
Posted: April 08 2010 at 22:30 | IP Logged Quote andyR

Thanks for the quick reply. Nice to know that a newbie like me has a place to get questions answers.

To address your second question first, all these devices on my network are Icon switches connected to a 2414u PLC. As to something triggering the peek, I can't see anything. Here is a somewhat shortened version of the event log from when I restarted PH this evening (all I deleted were some similar events to keep this post somewhat reasonable in terms of length)

4/8/2010 20:11:06:802,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[0B.02.43] To Address:[0A.A2.0E] Flags:[38] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: KITCHEN NOOK To: POWERLINC1, Peek Addr",,55,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:11:05:848,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[0B.02.43] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: KITCHEN NOOK To: POWERLINC1, Peek Addr",,54,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:11:05:113,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[0B.02.43] To Address:[0A.A2.0E] Flags:[35] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: KITCHEN NOOK To: POWERLINC1, Set Addr MSB",,53,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:52:376,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.29.B1] To Address:[0A.A2.0E] Flags:[38] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: KITCHEN MAIN NORTH To: POWERLINC1, Peek Addr",,52,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:51:331,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.29.B1] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: KITCHEN MAIN NORTH To: POWERLINC1, Peek Addr",,51,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:50:594,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.29.B1] To Address:[0A.A2.0E] Flags:[38] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: KITCHEN MAIN NORTH To: POWERLINC1, Set Addr MSB",,50,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:38:732,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.2D.40] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: LOWER STAIRS To: POWERLINC1, Peek Addr",,49,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:38,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.2D.40] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: LOWER STAIRS To: POWERLINC1, Peek Addr",,48,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:37:361,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.2D.40] To Address:[0A.A2.0E] Flags:[33] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: LOWER STAIRS To: POWERLINC1, Set Addr MSB",,47,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:25:023,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.67.C5] To Address:[0A.A2.0E] Flags:[37] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: ANNA BEDROOM To: POWERLINC1, Peek Addr",,46,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:24:39,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.67.C5] To Address:[0A.A2.0E] Flags:[37] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: ANNA BEDROOM To: POWERLINC1, Peek Addr",,45,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:10:23:75,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.67.C5] To Address:[0A.A2.0E] Flags:[37] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: ANNA BEDROOM To: POWERLINC1, Set Addr MSB",,44,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:09:11:151,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.64.02] To Address:[0A.A2.0E] Flags:[37] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: BECCA BEDROOM To: POWERLINC1, Peek Addr",,31,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:09:10:502,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.64.02] To Address:[0A.A2.0E] Flags:[37] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: BECCA BEDROOM To: POWERLINC1, Peek Addr",,30,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:09:09:855,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.64.02] To Address:[0A.A2.0E] Flags:[37] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: BECCA BEDROOM To: POWERLINC1, Set Addr MSB",,29,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:58:34,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.6A.1D] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[12]. Decode: Direct ACK. From: MASTER BATH To: POWERLINC1, Peek Addr",,28,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:57:703,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.6A.1D] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[12]. Decode: Direct ACK. From: MASTER BATH To: POWERLINC1, Peek Addr",,27,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:57:059,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[04.6A.1D] To Address:[0A.A2.0E] Flags:[43] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: MASTER BATH To: POWERLINC1, Set Addr MSB",,26,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:31:373,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.28.7C] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: UPPER HALL MIDDLE To: POWERLINC1, Peek Addr",,22,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:04:913,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.2D.3C] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: LOWER HALL BACK To: POWERLINC1, Peek Addr",,16,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:04:178,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.2D.3C] To Address:[0A.A2.0E] Flags:[43] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: LOWER HALL BACK To: POWERLINC1, Peek Addr",,15,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:08:02:784,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[11.2D.3C] To Address:[0A.A2.0E] Flags:[33] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: LOWER HALL BACK To: POWERLINC1, Set Addr MSB",,14,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:07:10:766,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[0B.02.43] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[0]. Decode: Direct ACK. From: KITCHEN NOOK To: POWERLINC1, Peek Addr",,4,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:07:10:032,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[0B.02.43] To Address:[0A.A2.0E] Flags:[33] Cmd1:[43] Cmd2:[32]. Decode: Direct ACK. From: KITCHEN NOOK To: POWERLINC1, Peek Addr",,3,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:07:09:299,30,"Incoming Insteon received on Insteon DM controller POWERLINC USB. From Address:[0B.02.43] To Address:[0A.A2.0E] Flags:[33] Cmd1:[40] Cmd2:[0]. Decode: Direct ACK. From: KITCHEN NOOK To: POWERLINC1, Set Addr MSB",,2,Insteon In,0,#000000,65280,#00ff00
4/8/2010 20:06:20:786,0,PowerHome System Startup.,,1,System Startup,16777215,#ffffff,255,#ff0000
4/7/2010 21:19:59:227,25,PowerHome System Shutdown,,411,System Shutdown,16777215,#ffffff,255,#ff0000

The only thing I see besides the Peek Addr is that it seems like each of those events occurs after a 'Set Addr MSB', but that is also an "Insteon In" event.

Some more background that may help. I recently moved PH from the computer I was using for evaluating the program to a new system. I didn't have this issue on my old system, but that was an XP box that is getting a bit flakey. I moved the database directory and re-downloaded the app back on the PLC (not sure of that was necessary, but in my attempts to get rid of this issue, it didn't sound like it would hurt). Maybe I need to do something else?

Thanks again for helping out.

Andy
Back to Top View andyR's Profile Search for other posts by andyR
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 08 2010 at 23:14 | IP Logged Quote grif091

The Set MSB command is Set Most Significant Byte. This is the first command that is issued when reading device memory. The subsequent Peek commands set the Least Significant Byte of the memory address and the content of that memory location is returned. A Set MSB followed by two Peek commands are being issued to what looks like each device defined to the PLC. These activities are being initiated by the PLC itself, not explicitly by PowerHome2.   Not sure why. Since it is the PLC and not Powerhome issuing these commands I cannot tell what memory addresses are accessed. You can start SDM3 manually before starting Powerhome. Open the SDM3 window by double clicking on the blue T shaped ICON in the system tray before starting Powerhome. This may show the outbound commands being issued by the PLC. It has been a long time since I ran PowerHome with a PLC. I would assume that once the PLC has cycled through the devices defined to it this activity would stop.

You said you "downloaded the app back on the PLC". What app are you referring to.


__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 08 2010 at 23:25 | IP Logged Quote BeachBum

I might suggest you also download core apps and add min again since you reinstalled PH. May not fix it but just one more base to cover.

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 08 2010 at 23:42 | IP Logged Quote grif091

Pete has a good suggestion. The other thing that might provide some information is the Insteon Raw Log produced by PowerHome. The more I think about the Event Log the ACKs may be in response to something that Powerhome issued during initialization that it does not trace in the Event Log (as it does not trace background activity in the Event Log) but should show up in the Insteon Raw Log. One of the things that Powerhome does do is check the link database level to see if anything changed outside of Powerhome. That might be what is happening and would likely not be in the Event Log but should be in the Insteon Raw Log.

Do you run with the Status Scan option checked. If so turn it off and see if that stops the device activity.

__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 09 2010 at 09:25 | IP Logged Quote grif091

Andy, what release of PowerHome are you running? I turned on Status Scan (which I don't normally run with) and the Set MSB, Peek sequence is somewhat similar to yours in the Insteon Raw Log but I have no entries being logged in the Event Trace. I am running with a PLM so I cannot duplicate your environment exactly.

__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 09 2010 at 09:34 | IP Logged Quote BeachBum

Lee, I can’t help but think that the PLC is looping around with its DB because there may be a mismatch in its array. If you need me to test with a PLC I have that capability. We’ll just have to wait and see what Andy comes up with next.

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 09 2010 at 12:49 | IP Logged Quote grif091

Pete, I’m pretty sure what Andy is seeing is the normal Status Scan Set MSB, Peek, Peek sequence that is shown below. These are from my Insteon Raw Log file so they are top to bottom. Since the ACKs are not being traced in my Event Log it could be that PowerHome is logging the ACKs in the Event Log because it is a PLC (which is probably a bug) or perhaps Andy is not on 2.1b. If you are of a mind set to run with the PLC for a short test with Status Scan enabled it would show whether the ACK Event Log entries are only when using a PLC or there is some other variable involved on Andy’s system.   Seeing the Insteon Raw Log from Andy’s system I think will show that PowerHome is issuing the Set MSB, Peek, Peek sequence and the only question is why the ACK Event Log entries are being generated.

2010-04-09 12:10:07.079     TX  &nbs p;  02 62 04 56 81 05 28 00
2010-04-09 12:10:07.111     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 56 81 05 28 00 06
2010-04-09 12:10:07.642     RX  &nbs p;  RECEIVEINSTEONRAW=04 56 81 0F 44 DC 26 28 00
2010-04-09 12:10:07.673     TX  &nbs p;  02 62 04 56 81 05 2B 30
2010-04-09 12:10:07.704     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 56 81 05 2B 30 06
2010-04-09 12:10:07.939     RX  &nbs p;  RECEIVEINSTEONRAW=04 56 81 0F 44 DC 21 2B 20
2010-04-09 12:10:07.970     TX  &nbs p;  02 62 04 56 81 05 2B 31
2010-04-09 12:10:08.001     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 56 81 05 2B 31 06
2010-04-09 12:10:08.220     RX  &nbs p;  RECEIVEINSTEONRAW=04 56 81 0F 44 DC 21 2B 00


2010-04-09 12:10:18.392     TX  &nbs p;  02 62 04 5B 2A 0F 19 00
2010-04-09 12:10:18.423     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 5B 2A 0F 19 00 06
2010-04-09 12:10:18.736     RX  &nbs p;  RECEIVEINSTEONRAW=04 5B 2A 0F 44 DC 2B 02 00


2010-04-09 12:10:18.783     TX  &nbs p;  02 62 04 5B 2A 05 28 00
2010-04-09 12:10:18.814     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 5B 2A 05 28 00 06
2010-04-09 12:10:19.079     RX  &nbs p;  RECEIVEINSTEONRAW=04 5B 2A 0F 44 DC 21 28 00
2010-04-09 12:10:19.111     TX  &nbs p;  02 62 04 5B 2A 05 2B 30
2010-04-09 12:10:19.142     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 5B 2A 05 2B 30 06
2010-04-09 12:10:19.345     RX  &nbs p;  RECEIVEINSTEONRAW=04 5B 2A 0F 44 DC 21 2B 20
2010-04-09 12:10:19.376     TX  &nbs p;  02 62 04 5B 2A 05 2B 31
2010-04-09 12:10:19.408     RX  &nbs p;  SENTINSTEON=0F 44 DC 04 5B 2A 05 2B 31 06
2010-04-09 12:10:19.626     RX  &nbs p;  RECEIVEINSTEONRAW=04 5B 2A 0F 44 DC 21 2B 00


__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 09 2010 at 14:13 | IP Logged Quote BeachBum

Lee, I’ll test that this weekend if Andy doesn’t provide more insight be between now and then.

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 09 2010 at 15:49 | IP Logged Quote BeachBum


Here you go Lee. No ACK messages coming to PH. Scan was off.

DownloadTimer started
timerActivate enabled
UI:ConnectedAndReady
SDM:DM=active,1.01.138.308,4/9/2010 2:42:48 PM,responded,08.9F.6F,2.13,xdevices=True
starttime=00:07
ui:getplcstatus
PLC:getPLCstatus=beginlist
port=USB4
connected=True
firmware=2.13
id=08.9F.6F
devicetype=InsteonPLC-USB
lastErrorMsg=#0:
endlist
uifinished:getplcstatus
ui:getlinks
uifinished:getlinks
ProgressStart
ProgressMax=1024
Progress=0%,0,1024
Progress=12%,128,1024
Progress=25%,256,1024
Progress=37%,384,1024
Progress=50%,512,1024
Progress=62%,640,1024
Progress=75%,768,1024
Progress=87%,896,1024
ProgressEnd=True
PLC:getlinks=beginlist
id=08.24.F7,mode=sla,addr=FC20,laddr=0000,g=1,cmds=00 00,d=00
id=0D.4F.EE,mode=sla,addr=FC40,laddr=0000,g=1,cmds=00 00,d=00
id=0E.A1.EC,mode=sla,addr=FC48,laddr=0000,g=1,cmds=00 00,d=00
id=0F.A5.EB,mode=sla,addr=FC50,laddr=0000,g=1,cmds=00 00,d=00
id=0C.04.E0,mode=sla,addr=FC78,laddr=0000,g=1,cmds=00 00,d=00
id=0A.00.DF,mode=sla,addr=FC80,laddr=0000,g=1,cmds=00 00,d=00
id=0D.03.DC,mode=sla,addr=FC88,laddr=0000,g=1,cmds=00 00,d=00
id=0E.9B.D7,mode=sla,addr=FCA0,laddr=0000,g=1,cmds=00 00,d=00
id=0D.01.D5,mode=sla,addr=FCA8,laddr=0000,g=1,cmds=00 00,d=00
id=0A.02.CC,mode=sla,addr=FCC8,laddr=0000,g=1,cmds=00 00,d=00
id=11.8C.C6,mode=sla,addr=FCE0,laddr=0000,g=1,cmds=00 00,d=00
id=0E.A0.C0,mode=sla,addr=FCF8,laddr=0000,g=1,cmds=00 00,d=00
id=0E.7A.B7,mode=sla,addr=FD20,laddr=0000,g=1,cmds=00 00,d=00
id=0A.3D.B3,mode=sla,addr=FD30,laddr=0000,g=1,cmds=00 00,d=00
id=09.50.A3,mode=sla,addr=FD70,laddr=0000,g=1,cmds=00 00,d=00
id=0E.A3.95,mode=sla,addr=FDA8,laddr=0000,g=1,cmds=00 00,d=00
id=04.BB.8F,mode=sla,addr=FDC0,laddr=0000,g=1,cmds=00 00,d=00
id=0A.96.83,mode=sla,addr=FDF0,laddr=0000,g=1,cmds=00 00,d=00
id=09.42.7F,mode=sla,addr=FE00,laddr=0000,g=1,cmds=00 00,d=00
id=0B.FD.6A,mode=sla,addr=FE50,laddr=0000,g=1,cmds=00 00,d=00
id=0E.7A.61,mode=sla,addr=FE78,laddr=0000,g=1,cmds=00 00,d=00
id=08.27.56,mode=sla,addr=FEA0,laddr=F9E0,g=1,cmds=00 00,d=00
id=0F.C5.57,mode=sla,addr=F9E0,laddr=0000,g=1,cmds=00 00,d=00
id=0D.0D.52,mode=sla,addr=FEB0,laddr=0000,g=1,cmds=00 00,d=00
id=04.D0.45,mode=sla,addr=FEE8,laddr=0000,g=1,cmds=00 00,d=00
id=0E.7A.42,mode=sla,addr=FEF0,laddr=0000,g=1,cmds=00 00,d=00
id=0A.1F.40,mode=sla,addr=FEF8,laddr=0000,g=1,cmds=00 00,d=00
id=04.B0.31,mode=sla,addr=FF38,laddr=0000,g=1,cmds=00 00,d=00
id=0E.9E.23,mode=sla,addr=FF70,laddr=0000,g=1,cmds=00 00,d=00
id=09.43.1F,mode=sla,addr=FF80,laddr=0000,g=1,cmds=00 00,d=00
id=0E.9D.19,mode=sla,addr=FF98,laddr=0000,g=1,cmds=00 00,d=00
id=0A.03.13,mode=sla,addr=FFB0,laddr=0000,g=1,cmds=00 00,d=00
id=0A.FB.06,mode=sla,addr=FFE0,laddr=0000,g=1,cmds=00 00,d=00
id=0E.A5.02,mode=sla,addr=FFF0,laddr=0000,g=1,cmds=00 00,d=00
endlist
ui:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F
si:00 00 00 0F 00 F5 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 25 28 0F
4/9/2010 2:43:05 PM:ackmsg=0F 00 F5 08 9F 6F 25 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F 00 F5 05 2B F8
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 2B F8
si:00 00 00 0F 00 F5 05 2B F8
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 21 2B 02
4/9/2010 2:43:06 PM:ackmsg=0F 00 F5 08 9F 6F 21 2B 02
ui:sendinsteonraw=00 00 00 0E A0 C0 0F 11 FF
uifinished:sendinsteonraw=00 00 00 0E A0 C0 0F 11 FF
si:00 00 00 0E A0 C0 0F 11 FF
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0E A0 C0 08 9F 6F 2B 11 FF
4/9/2010 2:43:09 PM:ackmsg=0E.A0.C0:ON at ON
PLC:eventraw=03
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0E A0 C0 0F 13 00
uifinished:sendinsteonraw=00 00 00 0E A0 C0 0F 13 00
si:00 00 00 0E A0 C0 0F 13 00
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0E A0 C0 08 9F 6F 2F 13 00
4/9/2010 2:43:12 PM:ackmsg=0E.A0.C0:OFF at OFF
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F
si:00 00 00 0F 00 F5 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 26 28 0F
4/9/2010 2:43:17 PM:ackmsg=0F 00 F5 08 9F 6F 26 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F 00 F5 05 2B F0
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 2B F0
si:00 00 00 0F 00 F5 05 2B F0
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 26 2B 00
4/9/2010 2:43:18 PM:ackmsg=0F 00 F5 08 9F 6F 26 2B 00
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 28 0F
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 28 0F
si:00 00 00 0F C5 57 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 28 0F
4/9/2010 2:43:29 PM:ackmsg=0F C5 57 08 9F 6F 25 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F8
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F8
si:00 00 00 0F C5 57 05 2B F8
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B A2
4/9/2010 2:43:29 PM:ackmsg=0F C5 57 08 9F 6F 25 2B A2
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F9
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F9
si:00 00 00 0F C5 57 05 2B F9
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 01
4/9/2010 2:43:30 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 01
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FA
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FA
si:00 00 00 0F C5 57 05 2B FA
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 0F
4/9/2010 2:43:31 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FB
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FB
si:00 00 00 0F C5 57 05 2B FB
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 42
4/9/2010 2:43:31 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 42
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FC
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FC
si:00 00 00 0F C5 57 05 2B FC
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 4E
4/9/2010 2:43:32 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 4E
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FD
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FD
si:00 00 00 0F C5 57 05 2B FD
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B FF
4/9/2010 2:43:33 PM:ackmsg=0F C5 57 08 9F 6F 25 2B FF
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FE
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FE
si:00 00 00 0F C5 57 05 2B FE
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 1F
4/9/2010 2:43:33 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 1F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FF
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FF
si:00 00 00 0F C5 57 05 2B FF
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 01
4/9/2010 2:43:34 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 01
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 28 0F
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 28 0F
si:00 00 00 0F C5 57 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 28 0F
4/9/2010 2:43:45 PM:ackmsg=0F C5 57 08 9F 6F 25 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F0
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F0
si:00 00 00 0F C5 57 05 2B F0
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B A2
4/9/2010 2:43:46 PM:ackmsg=0F C5 57 08 9F 6F 25 2B A2
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F1
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F1
si:00 00 00 0F C5 57 05 2B F1
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 02
4/9/2010 2:43:46 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 02
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F2
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F2
si:00 00 00 0F C5 57 05 2B F2
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 0F
4/9/2010 2:43:47 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F3
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F3
si:00 00 00 0F C5 57 05 2B F3
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 42
4/9/2010 2:43:48 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 42
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F4
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F4
si:00 00 00 0F C5 57 05 2B F4
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 4E
4/9/2010 2:43:48 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 4E
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F5
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F5
si:00 00 00 0F C5 57 05 2B F5
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B FF
4/9/2010 2:43:49 PM:ackmsg=0F C5 57 08 9F 6F 25 2B FF
PLC:eventraw=03

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 09 2010 at 18:06 | IP Logged Quote grif091

Thanks Pete. These commands are looking at the link database link records of 0F.00.F5, followed by an Insteon ON/Off command sequence to 0E.A0.C0, followed by commands looking at the link database link records of 0F.C5.57. I added comments at each Outbound and Inbound sequence as to what is happening. The commands associated with checking the link database level are not in this sequence (Set MSB, Peek, Peek of database level).

ui:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F   *** Outbound Set MSB 0x0F to 0F.00.F5 – this is the MSB for the link database
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F
si:00 00 00 0F 00 F5 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 25 28 0F *** Inbound ACK of Set MSB from 0F.00.F5 to 08.9F.6F
4/9/2010 2:43:05 PM:ackmsg=0F 00 F5 08 9F 6F 25 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F 00 F5 05 2B F8 *** Outbound Peek 0xF8 to 0F.00.F5 – this is the address of the Flag byte for the first link record
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 2B F8
si:00 00 00 0F 00 F5 05 2B F8
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 21 2B 02 *** Inbound ACK of Peek from 0F.00.F5 to 08.9F.6F – Flag byte is 02 which is an inactive link record
4/9/2010 2:43:06 PM:ackmsg=0F 00 F5 08 9F 6F 21 2B 02
ui:sendinsteonraw=00 00 00 0E A0 C0 0F 11 FF *** Outbound ON command to 0E.A0.C0
uifinished:sendinsteonraw=00 00 00 0E A0 C0 0F 11 FF
si:00 00 00 0E A0 C0 0F 11 FF
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0E A0 C0 08 9F 6F 2B 11 FF *** Inbound ACK of ON command from 0E.A0.C0 to 08.9F.6F
4/9/2010 2:43:09 PM:ackmsg=0E.A0.C0:ON at ON
PLC:eventraw=03
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0E A0 C0 0F 13 00 *** Outbound OFF command to 0E.A0.C0
uifinished:sendinsteonraw=00 00 00 0E A0 C0 0F 13 00
si:00 00 00 0E A0 C0 0F 13 00
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0E A0 C0 08 9F 6F 2F 13 00 *** Inbound ACK of OFF command from 0E.A0.C0 to 08.9F.6F
4/9/2010 2:43:12 PM:ackmsg=0E.A0.C0:OFF at OFF
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F *** Outbound Set MSB 0x0F to 0F.00.F5 – this is the MSB for the link database

uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 28 0F
si:00 00 00 0F 00 F5 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 26 28 0F *** Inbound ACK of Set MSB from 0F.00.F5 to 08.9F.6F
4/9/2010 2:43:17 PM:ackmsg=0F 00 F5 08 9F 6F 26 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F 00 F5 05 2B F0
uifinished:sendinsteonraw=00 00 00 0F 00 F5 05 2B F0 *** Outbound Peek 0xF0 to 0F.00.F5 – this is the address of the Flag byte for the second link record
si:00 00 00 0F 00 F5 05 2B F0
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F 00 F5 08 9F 6F 26 2B 00 *** Inbound ACK of Peek from 0F.00.F5 to 08.9F.6F – Flag byte is 00 which is End Of List link record
4/9/2010 2:43:18 PM:ackmsg=0F 00 F5 08 9F 6F 26 2B 00
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 28 0F *** Outbound Set MSB 0x0F to 0F.C5.57 – this is the MSB for the link database
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 28 0F
si:00 00 00 0F C5 57 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 28 0F *** Inbound ACK of Set MSB from 0F.C5.57 to 08.9F.6F
4/9/2010 2:43:29 PM:ackmsg=0F C5 57 08 9F 6F 25 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F8 *** Outbound Peek 0xF8 to 0F.C5.57 – this is the address of the Flag byte for the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F8
si:00 00 00 0F C5 57 05 2B F8
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B A2 *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – Flag byte is A2 which is an active link record
4/9/2010 2:43:29 PM:ackmsg=0F C5 57 08 9F 6F 25 2B A2
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F9 *** Outbound Peek 0xF9 to 0F.C5.57 – this is the address of the 2nd byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F9
si:00 00 00 0F C5 57 05 2B F9
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 01 *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 2nd byte is 0x01 which is Group 1
4/9/2010 2:43:30 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 01
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FA *** Outbound Peek 0xFA to 0F.C5.57 – this is the address of the 3rd byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FA
si:00 00 00 0F C5 57 05 2B FA
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 0F *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 3rd byte is 0x0F which is 1st byte of device address
4/9/2010 2:43:31 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FB *** Outbound Peek 0xFB to 0F.C5.57 – this is the address of the 4th byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FB
si:00 00 00 0F C5 57 05 2B FB
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 42 *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 4th byte is 0x42 which is 2nd byte of device address
4/9/2010 2:43:31 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 42
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FC *** Outbound Peek 0xFC to 0F.C5.57 – this is the address of the 5th byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FC
si:00 00 00 0F C5 57 05 2B FC
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 4E *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 5th byte is 0x4E which is 3rd byte of device address
4/9/2010 2:43:32 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 4E
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FD *** Outbound Peek 0xFD to 0F.C5.57 – this is the address of the 6th byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FD
si:00 00 00 0F C5 57 05 2B FD
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B FF *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 6th byte is 0xFF which is LD1 Bright level
4/9/2010 2:43:33 PM:ackmsg=0F C5 57 08 9F 6F 25 2B FF
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FE *** Outbound Peek 0xFE to 0F.C5.57 – this is the address of the 7th byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FE
si:00 00 00 0F C5 57 05 2B FE
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 1F *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 7th byte is 0x1F which is LD2 Ramp rate
4/9/2010 2:43:33 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 1F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B FF *** Outbound Peek 0xFF to 0F.C5.57 – this is the address of the 8th byte of the first link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B FF
si:00 00 00 0F C5 57 05 2B FF
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 01 *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – 8th byte is 0x01 which is LD3 Unit number
4/9/2010 2:43:34 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 01
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 28 0F *** Outbound Set MSB 0x0F to 0F.C5.57 – this is the MSB for the link database
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 28 0F
si:00 00 00 0F C5 57 05 28 0F
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 28 0F *** Inbound ACK of Set MSB from 0F.C5.57 to 08.9F.6F
4/9/2010 2:43:45 PM:ackmsg=0F C5 57 08 9F 6F 25 28 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F0 *** Outbound Peek 0xF0 to 0F.C5.57 – this is the address of the Flag byte for the second link record
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F0
si:00 00 00 0F C5 57 05 2B F0
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B A2 *** Inbound ACK of Peek from 0F.C5.57 to 08.9F.6F – Flag byte is A2 which is an active link record
4/9/2010 2:43:46 PM:ackmsg=0F C5 57 08 9F 6F 25 2B A2
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F1
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F1
si:00 00 00 0F C5 57 05 2B F1
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 02
4/9/2010 2:43:46 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 02
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F2
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F2
si:00 00 00 0F C5 57 05 2B F2
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 0F
4/9/2010 2:43:47 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 0F
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F3
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F3
si:00 00 00 0F C5 57 05 2B F3
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 42
4/9/2010 2:43:48 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 42
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F4
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F4
si:00 00 00 0F C5 57 05 2B F4
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B 4E
4/9/2010 2:43:48 PM:ackmsg=0F C5 57 08 9F 6F 25 2B 4E
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 0F C5 57 05 2B F5
uifinished:sendinsteonraw=00 00 00 0F C5 57 05 2B F5
si:00 00 00 0F C5 57 05 2B F5
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 0F C5 57 08 9F 6F 25 2B FF
4/9/2010 2:43:49 PM:ackmsg=0F C5 57 08 9F 6F 25 2B FF
PLC:eventraw=03


__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
andyR
Newbie
Newbie


Joined: April 07 2010
Online Status: Offline
Posts: 15
Posted: April 09 2010 at 21:57 | IP Logged Quote andyR

A lot of interesting posts, some of which I didn't quite follow. However, I did start the SDM by itself, and the log window shows that things are very quiet until I start PH. At that point a lot of activity shows up until I quit PH again. Here is a snippet:

4/9/2010 7:35:37 PM:ackmsg=11 2D 3C 0A A2 0E 25 2B 20
PLC:p30:SRIR=04,11 2D 3C 0A A2 0E 25 2B 20
PLC:eventraw=03
ui:p31:srir=00 00 00 11 2D 3C 05 2B 31
uifinished:p31:srir=00 00 00 11 2D 3C 05 2B 31
si:0A A2 0E 11 2D 3C 05 2B 31
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 2D 3C 0A A2 0E 25 2B 00
4/9/2010 7:35:38 PM:ackmsg=11 2D 3C 0A A2 0E 25 2B 00
PLC:eventraw=03
PLC:p31:SRIR=03,11 2D 3C 0A A2 0E 25 2B 00
ui:srq:srir=00 00 00 11 28 75 0F 19 00
uifinished:srq:srir=00 00 00 11 28 75 0F 19 00
si:0A A2 0E 11 28 75 0F 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 2B 06 00
4/9/2010 7:35:49 PM:ackmsg=11 28 75 0A A2 0E 2B 06 00
PLC:srq:SRIR=04,11 28 75 0A A2 0E 2B 06 00
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 11 28 75 05 28 00
uifinished:sendinsteonraw=00 00 00 11 28 75 05 28 00
si:00 00 00 11 28 75 05 28 00
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 21 28 00
4/9/2010 7:35:50 PM:ackmsg=11 28 75 0A A2 0E 21 28 00
ui:p30:srir=00 00 00 11 28 75 05 2B 30
uifinished:p30:srir=00 00 00 11 28 75 05 2B 30
si:0A A2 0E 11 28 75 05 2B 30
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 21 2B 20
4/9/2010 7:35:50 PM:ackmsg=11 28 75 0A A2 0E 21 2B 20
PLC:p30:SRIR=04,11 28 75 0A A2 0E 21 2B 20
ui:p31:srir=00 00 00 11 28 75 05 2B 31
uifinished:p31:srir=00 00 00 11 28 75 05 2B 31
si:0A A2 0E 11 28 75 05 2B 31
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 21 2B 00
4/9/2010 7:35:51 PM:ackmsg=11 28 75 0A A2 0E 21 2B 00
PLC:p31:SRIR=04,11 28 75 0A A2 0E 21 2B 00

Not sure what to make of it yet, but it looks like it is some interaction between PH and the PLC.

I've tried downloading the 'core app' several times, with and without doing a subsequent 'add min'. I'm about to try clearing out the links as well and then letting it rediscover these.
When I look at the raw logs, I do seen an occasional TX command float by, amid a sea of RXs. The TX command is a 'p31:srir=...." where .... is a set of 9 8-bit groups in hex.   Actually, there are also other TX cmds. I see a 'sendinsteonraw=....' and a 'srq:srir'. No idea what these mean, and none of these get reflected in the event log.
I'd be happy to provide more information, but I'm not sure what is required. Oh, and since somebody asked, I'm running PH 2.1b, which I think is the latest one. I also usually run with status-scan off, which was another question.

Thanks again.

andy
Back to Top View andyR's Profile Search for other posts by andyR
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 09 2010 at 23:16 | IP Logged Quote BeachBum

My guess is you won’t see any activity until PH is started. I would suggest that is normal. What isn’t is your seeing activity in the Event Log without accompanying Insteon Outgoing.

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 10 2010 at 04:09 | IP Logged Quote grif091

Andy, This is standard “Status Scan” activity of Powerhome. It checks the status of each device and whether the link database level has changed. The Powerhome “Insteon Raw Log” will show the same Outbound and Inbound activity.

If you did not see this activity on your previous PH install you had the “Status Scan” option turned off. I do not run with Status Scan option set because of the volume of Insteon traffic it generates.

What release of Powerhome are you running? The only question is why the ACKs are being traced in your Event Log as they are not traced in my Event Log on 2.1b. The underlying Insteon message traffic is expected with Status Scan.



4/9/2010 7:35:37 PM:ackmsg=11 2D 3C 0A A2 0E 25 2B 20
PLC:p30:SRIR=04,11 2D 3C 0A A2 0E 25 2B 20
PLC:eventraw=03
ui:p31:srir=00 00 00 11 2D 3C 05 2B 31 *** Outbound Peek 0x31 to 11.2D.3C
uifinished:p31:srir=00 00 00 11 2D 3C 05 2B 31
si:0A A2 0E 11 2D 3C 05 2B 31
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 2D 3C 0A A2 0E 25 2B 00 *** Inbound ACK of Peek data 0x00 from 11.2D.3C to 0A.A2.0E
4/9/2010 7:35:38 PM:ackmsg=11 2D 3C 0A A2 0E 25 2B 00
PLC:eventraw=03
PLC:p31:SRIR=03,11 2D 3C 0A A2 0E 25 2B 00
ui:srq:srir=00 00 00 11 28 75 0F 19 00 *** Outbound Status Query to 11.28.75
uifinished:srq:srir=00 00 00 11 28 75 0F 19 00
si:0A A2 0E 11 28 75 0F 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 2B 06 00 *** Inbound ACK of Status Query
4/9/2010 7:35:49 PM:ackmsg=11 28 75 0A A2 0E 2B 06 00
PLC:srq:SRIR=04,11 28 75 0A A2 0E 2B 06 00
PLC:eventraw=03
ui:sendinsteonraw=00 00 00 11 28 75 05 28 00 *** Outbound Set MSB 0x00 to 11.28.75
uifinished:sendinsteonraw=00 00 00 11 28 75 05 28 00
si:00 00 00 11 28 75 05 28 00
PLC:sendinsteonraw=True
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 21 28 00 *** Inbound ACK of Set MSB from 11.28.75 to 0A.A2.0E
4/9/2010 7:35:50 PM:ackmsg=11 28 75 0A A2 0E 21 28 00
ui:p30:srir=00 00 00 11 28 75 05 2B 30   *** Outbound Peek 0x30 to 11.28.75
uifinished:p30:srir=00 00 00 11 28 75 05 2B 30
si:0A A2 0E 11 28 75 05 2B 30
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 21 2B 20 *** Inbound ACK of Peek data 0x20 from 11.28.75 to 0A.A2.0E
4/9/2010 7:35:50 PM:ackmsg=11 28 75 0A A2 0E 21 2B 20
PLC:p30:SRIR=04,11 28 75 0A A2 0E 21 2B 20
ui:p31:srir=00 00 00 11 28 75 05 2B 31 *** Outbound Peek 0x31 to 11.28.75
uifinished:p31:srir=00 00 00 11 28 75 05 2B 31
si:0A A2 0E 11 28 75 05 2B 31
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=04 11 28 75 0A A2 0E 21 2B 00 *** Inbound ACK of Peek data 0x00 from 11.28.75 to 0A.A2.0E
4/9/2010 7:35:51 PM:ackmsg=11 28 75 0A A2 0E 21 2B 00
PLC:p31:SRIR=04,11 28 75 0A A2 0E 21 2B 00


__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 10 2010 at 08:31 | IP Logged Quote BeachBum

Lee, Andy is running 2.1B. Andy, is Insteon Out checked in the Setup Logs screen? Check the Insteon Explorer and make sure Status Scan is unchecked. Then resubmit an Event Log without editing it.

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
andyR
Newbie
Newbie


Joined: April 07 2010
Online Status: Offline
Posts: 15
Posted: April 10 2010 at 10:40 | IP Logged Quote andyR

I tried a couple more things last night that didn't yield anything. On a whim, I tried moving the database directory out of the way, and copying an old version in, and that seemed to do the trick; I'm no longer getting the Peeks. I must have messed up something when transferring the database to my new system. I still have the old database (corrupt) directory, and I may play with it at a future data to see what is going on, but right now I'm just happy to be able to make forward progress again.
Thank you all for your help.

andy
Back to Top View andyR's Profile Search for other posts by andyR
 
grif091
Super User
Super User


Joined: March 26 2008
Location: United States
Online Status: Offline
Posts: 1357
Posted: April 10 2010 at 11:12 | IP Logged Quote grif091

Now that you are running on the old database, under Maintenance/Insteon Explorer, check the Enable Pending and Status Scan options in the upper left corner of the Insteon Explorer display. I would expect at least the Status Scan option is not checked. If/when you play with the other database, see whether the Status Scan option is checked in the new database.

__________________
Lee G
Back to Top View grif091's Profile Search for other posts by grif091
 
BeachBum
Super User
Super User
Avatar

Joined: April 11 2007
Location: United States
Online Status: Offline
Posts: 1880
Posted: April 10 2010 at 11:39 | IP Logged Quote BeachBum

Now we are making progress. If you go back to the other DB run the phupg exe before you reuse it.

__________________
Pete - X10 Oldie
Back to Top View BeachBum's Profile Search for other posts by BeachBum
 
andyR
Newbie
Newbie


Joined: April 07 2010
Online Status: Offline
Posts: 15
Posted: April 12 2010 at 22:05 | IP Logged Quote andyR

You are right; the status scan options and enable pending are not checked in the current DB. I was pretty sure I checked and they weren't enabled in the other DB either, but I wouldn't swear to it. When I actually stop being a chicken and pull up the other DB again (things are just working so nicely right now...) I'll check that and then also run phupg.exe to see what that does.
Thanks again for your help.

andy
Back to Top View andyR's Profile Search for other posts by andyR
 

If you wish to post a reply to this topic you must first login
If you are not already registered you must first register

  Post ReplyPost New Topic
Printable version Printable version

Forum Jump
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot delete your posts in this forum
You cannot edit your posts in this forum
You cannot create polls in this forum
You cannot vote in polls in this forum