Author |
|
Elecrick Newbie
Joined: April 16 2006
Online Status: Offline Posts: 3
|
Posted: April 16 2006 at 11:07 | IP Logged
|
|
|
The Insteon auto discover feature of the PowerHome program is not working. I just downloaded the program yesterday as recommended by a SmartHome rep. I am trying out the program and have not yet purchased it. Is auto discover deactivated until purchase?
I have tried to auto discover both keypad links and 1000W switches.
I am able to add the Insteon devices manually (although there is a required linking step "add IDs to PLC" in the Insteon DM control box that does not appear to have been well documented). I can control the devices added through Power Home and can view their status in Power Home even when controlled locally. This verifies that the program and the USB controller can communicate with the devices.
Please advise.
|
Back to Top |
|
|
dhoward Admin Group
Joined: June 29 2001 Location: United States
Online Status: Offline Posts: 4447
|
Posted: April 16 2006 at 23:02 | IP Logged
|
|
|
Elecrick,
Welcome to PowerHome!
The trial version is fully functional...no crippling.
Do you get anything in the SDM eventlog when trying to autodiscover?
If you can, paste the SDM log you get when doing the autodiscover. I may be able to pinpoint what is wrong. If you don't know how to get to the SDM log, just click on the SDM icon in your system tray (it's the "T" looking icon) and you'll have the SDM window open. You can then click on the button to save the logs.
Let me know and Im sure we'll get it fixed.
Dave.
|
Back to Top |
|
|
Elecrick Newbie
Joined: April 16 2006
Online Status: Offline Posts: 3
|
Posted: April 17 2006 at 06:18 | IP Logged
|
|
|
Dave,
Thank you for your quick response. The following is the event log from this morning. During this period I attempted to autodiscover four devices, but again the auto discover failed. In order, these were a switchlinc dimmer, switchlinc relay, keypadlinc and switchlinc dimmer. (None of these were previously attempted to be autodiscovered, nor had they been manually input.)
Note - I followed the instuctions exactly and after all devices were put in enrollment mode, I turned discover off, exited the DM control window and pressed F5.
log:DM=active,1.01.26.163,4/16/2006 8:14:06 AM,responded,00.D0.02,2.9
(continued)
...
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:07:13 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:07:28 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:07:43 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:07:58 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:08:13 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:08:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:08:43 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:09:13 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:09:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:09:43 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:09:58 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:10:13 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:10:28 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:10:43 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:10:58 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:11:13 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:11:28 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 80 41 2B 00 00
4/17/2006 5:11:43 AM:ackmsg=A0 02 46 00 80 41 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 04 91 82 B7 FB 2B 00 00
4/17/2006 5:11:58 AM:ackmsg=A0 04 91 82 B7 FB 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 7F E2 30 00 02 0F 2B 00 00
4/17/2006 5:12:13 AM:ackmsg=7F E2 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:12:28 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:12:43 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:12:58 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 04 91 81 20 10 2B 00 00
4/17/2006 5:13:13 AM:ackmsg=A0 04 91 81 20 10 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:13:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:13:43 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 34 02 0F 00 D0 02 2B 00 00
4/17/2006 5:13:58 AM:ackmsg=34 02 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:14:13 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 7F E2 30 00 02 0F 2B 00 00
4/17/2006 5:14:28 AM:ackmsg=7F E2 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:14:43 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:14:58 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:15:13 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 7F E2 30 00 02 0F 2B 00 00
4/17/2006 5:15:28 AM:ackmsg=7F E2 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 02 0F 2B 00 00
4/17/2006 5:15:43 AM:ackmsg=A0 02 46 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:15:58 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 02 0F 2B 00 00
4/17/2006 5:16:13 AM:ackmsg=A0 02 46 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 80 41 2B 00 00
4/17/2006 5:16:28 AM:ackmsg=A0 02 46 00 80 41 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:16:43 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 01 BF DF 2B 00 00
4/17/2006 5:16:58 AM:ackmsg=A0 02 46 01 BF DF 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 02 DF EF 2B 00 00
4/17/2006 5:17:13 AM:ackmsg=A0 02 46 02 DF EF 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:17:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:17:43 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 34 02 46 00 02 0F 2B 00 00
4/17/2006 5:17:58 AM:ackmsg=34 02 46 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 D0 02 2B 00 00
4/17/2006 5:18:13 AM:ackmsg=A0 02 46 00 D0 02 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=06
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=01
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=06 00 22 0F 00 D0 02 2B 00 00
PLC:receiveinsteonraw=01 00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 18 00 08 3C D0 02 E6 EA 80
4/17/2006 5:18:43 AM:ackmsg=18 00 08 3C D0 02 E6 EA 80
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:18:58 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:19:13 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:19:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 02 0F 2B 00 00
4/17/2006 5:19:43 AM:ackmsg=A0 02 46 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:19:58 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:20:13 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:20:28 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=FD
PLC:eventraw=FE
PLC:eventraw=FD
PLC:eventraw=FE
text=
PLC:salad=initialized
PLC:eventraw=00
PLC:eventraw=FE
PLC:srq:SRIR=send failed
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:20:45 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 7F D2 0F 00 D0 02 23 00 00
4/17/2006 5:20:58 AM:ackmsg=7F D2 0F 00 D0 02 23 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:21:13 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 FF FF 41 FF FF 00 00 FF FF
PLC:receiveinsteonraw=06 FF FF 41 FF FF 00 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 8F 41 FF FF 00 00 FF FF
PLC:receiveinsteonraw=06 00 8F 41 FF FF 00 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:21:59 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:22:13 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:22:43 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:22:58 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 34 04 91 80 D0 02 2B 00 00
4/17/2006 5:23:13 AM:ackmsg=34 04 91 80 D0 02 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 34 02 0F 00 D0 02 2B 00 00
4/17/2006 5:23:28 AM:ackmsg=34 02 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 22 0F 00 D0 02 2F 00 00
PLC:receiveinsteonraw=04 07 83 40 08 8C 00 00 83 C0
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:23:58 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:24:13 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:24:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:24:43 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 D0 02 2B 00 00
4/17/2006 5:24:58 AM:ackmsg=A0 02 30 00 D0 02 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:25:13 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 00 02 0F 2B 00 00
4/17/2006 5:25:28 AM:ackmsg=A0 02 46 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:25:43 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:25:58 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:26:13 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:26:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 20 78 00 D0 02 18 00 80 70 FF FF FF FF FF FF FF FF FF FF FF FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:26:58 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:27:13 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:27:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 7F E2 30 00 02 0F 2B 00 00
4/17/2006 5:27:43 AM:ackmsg=7F E2 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:27:58 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 06 DC FD BF DF 2B 00 00
4/17/2006 5:28:13 AM:ackmsg=A0 06 DC FD BF DF 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 46 01 BF DF 2B 00 00
4/17/2006 5:28:28 AM:ackmsg=A0 02 46 01 BF DF 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 04 91 83 6F F7 2B 00 00
4/17/2006 5:28:43 AM:ackmsg=A0 04 91 83 6F F7 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:28:58 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:29:13 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:29:28 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 2B 00 00
4/17/2006 5:29:43 AM:ackmsg=A0 02 30 00 02 0F 2B 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:29:58 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=06
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:receiveinsteonraw=06 FF FF 92 FF FF 0F 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 34 02 0F 00 D0 02 27 00 00
4/17/2006 5:30:29 AM:ackmsg=34 02 0F 00 D0 02 27 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=06
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:receiveinsteonraw=06 FF FF F0 FF FF 0F 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 A0 02 30 00 02 0F 27 00 00
4/17/2006 5:30:59 AM:ackmsg=A0 02 30 00 02 0F 27 00 00
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=06
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:receiveinsteonraw=06 00 22 92 0F FF 0F 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:31:28 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 23 00 00
4/17/2006 5:31:44 AM:ackmsg=00 22 0F 00 D0 02 23 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:eventraw=02
PLC:eventraw=03
PLC:eventraw=06
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 0B 19 00
PLC:receiveinsteonraw=06 00 22 DB E1 BF 2C 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:32:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:32:29 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:32:43 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=06,00 22 0F 00 D0 02 2F 00 00
PLC:receiveinsteonraw=06 FF FF 78 FF FF 02 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:srq:SRIR=send failed
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:32:59 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:33:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:33:28 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:srq:SRIR=send failed
PLC:eventraw=05
4/17/2006 5:33:45 AM:nakmsg
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:srq:SRIR=05
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:34:00 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:34:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:srq:SRIR=send failed
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:34:29 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:34:43 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:34:59 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:35:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=06,00 22 0F 00 D0 02 2F 00 00
PLC:receiveinsteonraw=06 FF FF DF FF FF FF 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 27 00 00
4/17/2006 5:35:28 AM:ackmsg=00 22 0F 00 D0 02 27 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 27 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:35:43 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:35:58 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:36:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:36:28 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:36:43 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:36:58 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:37:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:37:28 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:37:43 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:37:58 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:38:13 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:38:28 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:38:43 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:sendplc=02 40 01 6d 00 01 fe 92 ff
PLC:sendplc=02 40 01 6D 00 01 06
ui:sendplc=02 40 01 6d 00 01 fe 92 ff
PLC:sendplc=02 40 01 6D 00 01 06
PLC:eventraw=06
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 6B FF FF 01 00 FF FF
PLC:receiveinsteonraw=06 B4 5F FF FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 6B FF FF 22 00 FF FF
ui:sendplc=02 40 01 6d 00 01 fe 92 ff
PLC:sendplc=02 40 01 6D 00 01 06
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 3A FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 3A FF FF 26 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 24 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 7B 00 FF FF
PLC:eventraw=06
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 3A FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 00 FF FF 4C 00 FF FF
PLC:receiveinsteonraw=06 FF FF 3A FF FF 7B 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:44:56 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:45:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:45:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=06,00 22 0F 00 D0 02 2F 00 00
PLC:receiveinsteonraw=06 FF FF 0F FF FF 02 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:45:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:45:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=06
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 03 19 00
PLC:receiveinsteonraw=06 FF FF 40 FF FF 00 00 FF FF
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:46:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:46:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:46:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:47:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:47:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:47:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:47:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:48:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:48:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:48:41 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:48:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:49:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:49:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:49:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:49:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:50:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:50:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:50:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:50:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:51:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:51:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:51:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:51:55 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:52:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=06,00 22 0F 00 D0 02 2F 00 00
PLC:receiveinsteonraw=06 FF FF 83 FF FF 00 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:52:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:52:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:52:55 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:53:10 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:53:25 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=06,00 22 0F 00 D0 02 2F 00 00
PLC:receiveinsteonraw=06 FF FF 65 FF FF 02 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:53:40 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:53:56 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:EXCEPTION: Invalid pointer operation
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:54:11 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=06
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:54:26 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=06,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
PLC:receiveinsteonraw=06 00 22 0F 00 D0 02 23 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:54:42 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:54:57 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:55:12 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:55:27 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:55:42 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:55:57 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:srq:SRIR=send failed
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:56:26 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:56:27 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:56:42 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=02
PLC:eventraw=04
PLC:receiveinsteonraw=02 00 D0 02 00 22 0F 07 19 00
PLC:eventraw=03
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2B 00 00
4/17/2006 5:56:57 AM:ackmsg=00 22 0F 00 D0 02 2B 00 00
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2B 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:57:12 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:57:30 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:57:45 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:58:01 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:58:15 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:58:30 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:eventraw=03
PLC:srq:SRIR=03,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:58:45 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:59:00 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
si:00 D0 02 00 22 0F 0F 19 00
PLC:eventraw=04
PLC:receiveinsteonraw=04 00 22 0F 00 D0 02 2F 00 00
4/17/2006 5:59:15 AM:ackmsg=00 22 0F 00 D0 02 2F 00 00
PLC:srq:SRIR=04,00 22 0F 00 D0 02 2F 00 00
|
Back to Top |
|
|
dhoward Admin Group
Joined: June 29 2001 Location: United States
Online Status: Offline Posts: 4447
|
Posted: April 19 2006 at 22:58 | IP Logged
|
|
|
Rick,
Ok...took me a little while to go through the whole log but I found the important section. The important area where autodiscover was turned on and attempted is below:
ui:sendplc=02 40 01 6d 00 01 fe 92 ff
PLC:sendplc=02 40 01 6D 00 01 06
ui:sendplc=02 40 01 6d 00 01 fe 92 ff
PLC:sendplc=02 40 01 6D 00 01 06
PLC:eventraw=06
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 6B FF FF 01 00 FF FF
PLC:receiveinsteonraw=06 B4 5F FF FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 6B FF FF 22 00 FF FF
ui:sendplc=02 40 01 6d 00 01 fe 92 ff
PLC:sendplc=02 40 01 6D 00 01 06
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 3A FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 3A FF FF 26 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 24 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 0E FF FF 7B 00 FF FF
PLC:eventraw=06
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 3A FF FF 01 00 FF FF
PLC:eventraw=06
PLC:receiveinsteonraw=06 FF FF 00 FF FF 4C 00 FF FF
PLC:receiveinsteonraw=06 FF FF 3A FF FF 7B 00 FF FF
ui:srq:srir=00 00 00 00 22 0F 0F 19 00
In this section I can see where the PLC was placed in autodiscovery mode and then the receiving of several Insteon messages that look as if they're masked (The FF's in the 2nd and 3rd bytes of the address in the from/to fields). The first thing that comes to mind is what version of the PLC do you have? When you very first start PowerHome, the SDM log should look similar to:
Code:
downloadTimer started
timerActivate enabled
SDM:DM=active,1.01.26.163,4/19/2006 10:36:30 PM,responded,00.D3.41,2.12
ui:getplcstatus
PLC:getPLCstatus=beginlist
port=USB4
connected=True
firmware=2.12
id=00.D3.41
devicetype=InsteonPLC-USB
lastErrorMsg=#0:
endlist
|
|
|
You can see the firmware version above is 2.12. Earlier versions of PLC firmware will not work and SmartHome will swap your unit out for free if you don't have the latest.
The next thing that might possibly be wrong is did you download the TimerCoreApp06 SALad application? It's a button in the "Insteon DM Control" screen called "Download Core Application". If this app is not loaded in the PLC, it will not behave as expected.
The last possible anamoly is that it looks like the devices actually attempted to link to one another. When you did the autodiscover, did you place the device in enrollment mode (press and hold the "on" button for 10 seconds or press and hold "set" button for 3 seconds) until the link light was blinking and then immediately press either the "on" or "set" button to cancel link mode before visiting the next switch? If you left the device in enrollment mode when you moved to the next switch, you would have actually created a link between the devices.
Let me know.
Dave.
|
Back to Top |
|
|
Elecrick Newbie
Joined: April 16 2006
Online Status: Offline Posts: 3
|
Posted: April 19 2006 at 23:37 | IP Logged
|
|
|
Dave,
The firmware version of my PLC (Insteon V2 USB #2414U) is 2.9. Per your information, I presume this is the source of the problem. I will contact SmartHome to swap for a new one.
As to the other two possibilities, I had downloaded the core application and I cancelled link mode each time before moving on to the next device. So these are not the cause of the problem.
Thanks for the help. I will contact you after I try out a new PLC to give you an update.
Rick
|
Back to Top |
|
|
dhoward Admin Group
Joined: June 29 2001 Location: United States
Online Status: Offline Posts: 4447
|
Posted: April 19 2006 at 23:54 | IP Logged
|
|
|
Rick,
I was 90% sure that was it. The newer version 2.12 will no longer even show masked messages and they are ignored altogether.
This should definately take care of your problem. Ive got a couple of 2.9 version PLC's Ive got to send back for a refund as well.
Let me know how it goes once you get the new PLC as it should increase your reliability in other aspects as well.
Dave.
|
Back to Top |
|
|
|
|